Hi guys,

I used to use the 2DS with and power 832, that i just upgraded to a PC1864. I configured it with the DLS IV program, and i added the 8 zone modules expansion (5108).

I receive a email each time my motion sensor detect someting: security event: Zone 3 Tamper, and after that a Tamper Restoral.

But in my zone configuration, section 330 and 334 are desactivated (FF). On the web site of EZEZ, the zone following are all disabled.

If anyone had an idea... :)
thanks

Re: Too much email report of tamper

Posted: Mon Apr 16, 2012 8:48 pm
by GrandWizard
Hi Ben, it sounds like you've configured your zones incorrectly. There are four different states for a zone: Open, Close, Fault, and Tamper. I am by no means an expert but I would think that you may have configured your zones for end-of-line resistors and you don't have any installed.

Maybe some of the good folks on the forum will have more to add. Otherwise, there is a good DSC forum at http://www.diysecurityforum.com.

Don't bother with diyalaramforum, many of our users have reported being banned for mentioning that they owned an Envisalink.

Re: Too much email report of tamper

Posted: Tue Apr 17, 2012 10:44 am
by Ben
Ah thanks you gave me an idea...I've check section 013 and...

For some reason, the DLS software enabled double resistor instead of the default of one! That is also why everytime a motion sensor saw us in the house the panel was beeping each time, that was annoying :)

Thanks for pointing me in the right direction.

Re: Too much email report of tamper

Posted: Tue Apr 17, 2012 11:23 am
by GrandWizard
No problem, I'm very glad I didn't point you in the wrong direction!